Capacity (to do work) is measured in ampere-hours, how many amps can be supplied for a given time duration. In this case, 6 amps for 1 hour, or 3 amps for 2 hours, etc. However, this is an incomplete metric as losses (both internal and external) increase at successively higher amperage discharges, and so as to qualify, the discharge rate must be specified.
At no time should the discharge rate exceed a 10A rate, according to the manufacturer.
As mentioned, Capacity, is C. The units for C are (1/t) or in this case 1/hr. And so 0.2C is 0.2 (1/hr) * 6 Ah = 1.2 A. This means that the battery is rated to provide 6Ah of total capacity at a 1.2 A discharge rate (for 5 hours). Discharging at a higher rate will reduce the overall usable capacity, i.e. discharging at 6A will likely not result in 1 hour of life (maybe something more like 45 minutes but without more data, impossible to predict). Correspondingly, discharging at less than 1.2A will likely provide more than 6Ah of total usable capacity. Again, how much more cannot be accurately predicted without more information.
We can think of VA as Watts (W), the difference being watts is real power, whereas VA is apparent power. I will not delve into the nuances of such, as it beyond the scope of my reply. Suffice it to say, for what is nearly a purely resistive load (where the power factor is very near 1), VA and W ratings will be effectively the same.
Power delivered is A times V (at the load), making 1.2A * 24V (=28.8W) the recommend load for a 1.2A discharge at start of discharge. Keep in mind that as batteries discharge their output voltage decreases, and so for a constant power application (for example, at 28.8W draw) the amperage will increase over time – as voltage goes down, “current” goes up for an equivalent power delivery. What this means is that the battery will start at 1.2A delivery but will increase over the duration of the discharge, effectively exceeding the rated 0.2C, lessening the rated capacity, as it is a function of amperage.
The data point given to you of “[email protected]” is just a point. In order to more accurately estimate runtime, a discharge curve is required; perhaps available buried deeper in the product specs. The best you can do is estimate runtime and even with the discharge curve will have to integrate over time to get a more precise result (which would also require the voltage discharge curve for the underlying cells used in construction of the battery unit).
Best practice is to oversize your UPS for whatever may be the intended application while simultaneously taking into consideration both expected runtime and power delivery requirements.
Hope this helps.
Note: Lots of edits due to lots of type-o’s.