TL;DR
advice on battery type choice for UPS…Am I confused about the specs… high rate discharge?
Geographical context : Greece and/or rest of Europe
Looking for some clarification and advice so I can wrap my head around the UPS battery concept.
Fair worning…Imay have overthouight it all, and also, ups noob.
Was able to get a relatively good deal on eBay for my first UPS, for an APC Smart UPS 1000 (SMT1000I) with no batteries
Naturally I am looking to get fresh batteries, and of course would like to avoid paying the APC $$$ toll for their RBC
As per APC this particular model takes the RBC 6 (although I have seen mods that make it take the RBC7 tunring into an “XL”, but not sure if I want to go down that path)
I have been able to extract some details, but I would appreciate if any experienced UPS or Batterry gurus might be able to guide through the below and offer some peace of mind
-
Volts & Capacity: qty 2 x 12V 11Ah as per RBC 6 spec
1.1. I am assuming 11Ah per battery?
1.2. Searching for 12V 11Ah did not return anything, 12Ah and 15Ah seem more common here. Am I safe to assume that I could simply add in a different Ah battery, if it is of course 12V and the same form factor etc? and it would just alter the length of available runtime?
-
Terminals
2.1. cannot tell from RBC 6 spec sheet, these should be the classic Faston F2 correct?
-
This one is providing the most confusion and trepidation - Battery delineation: High rate discharge?
3.1. Is the high-rate discharge an imperative? Shops here do not seem to know what I am talking about, and all websites here tend to recommend the “regular” product range of batteries just 12V 12Ah 20HR. and any American or UK websites or eBay listings also tend to be the same, just the usual 12V 12Ah 20HR batteries
3.2. Trying to find High rate discharge variants here is basically impossible… example Yuasa NP1212 – easily found and what keeps getting recommended as compatible. However Yuasa has a “High rate” series “NPH”….???
3.3. Complete Noob here but doing some calc on the regular 20HR batteries gives me a C-state of 14…which is considered high rate discharge (according to google…I have no clue)
3.4. Basically…… Am I overthinking this and have I been misled by the High rate discharge thing? Should I just make sure it’s a relatively known brand name, is 12V 12Ah+ 20HR VRLA, and does not mention “deep cycle”? and be done with it?
3.5. Am just worried I don’t turn my homelab into a little unsolicited fireworks show if I put in the incorrect type discharge of battery. Please ELI5 if need be, this is a perfect learning opportunity for me
-
Alot of folks mention good sources and brands, but mostly US/UK based
4.1. Any chance someone has relatively reputable brands and or sites for European suppliers?
4.2. Yuasa? ultracell? Invictus? Anyone familiar with those?
-
Other
5.1. Is there something I need to check if and when they arrive?
5.2. Is there a rudimentary way to check they are in good condition?
5.3. Is there something specific I need to do after I replace the batteries. either to the batteries themselves or on the ups, like a reset, or conditioning or something? or do I just plug in the new batteries do the little self-test on the ups, update battery change date, and away we go?
Thank you for any advice
Here’s your replacement RBC6 compatible battery set:
Sorry, it’s in Dutch, but therefore in EU land
There’s an email address on top of the page, contact them about shipping to Greece, although I assume it won’t be much of a problem (except for costs). This is a reliable shop, purchased from them for my own UPS’s and electric tools.
As for the rest: yes IMO you’re overthinking this. But your concerns are valid, especially when one doesn’t have either the experience or knowledge to make informed decisions.
HTH!
Thank you for the feedbakc 
it helped my go down a little rabbit hole and finally get some guidance.
Batterie shav ebeen bought and installed and are working perfectly fine
for posterity i have added my findings below…see italic bold
- Volts & Capacity: qty 2 x 12V 11Ah as per RBC 6 spec
- I am assuming 11Ah per battery?
- Yes, the Ah stated in RBC 6 is indeed 11 Ah per battery
- Searching for 12V 11Ah did not return anything, 12Ah and 15Ah seem more common here. Am I safe to assume that I could simply add in a different Ah battery, if it is of course 12V and the same form factor etc? and it would just alter the length of available runtime?
- Yes, it is safe, Ah capacity only affects your available run time on the UPS. Assuming you have correct V, dimensions, terminals and battery type of course)
- Terminals
- cannot tell from RBC 6 spec sheet, these should be the classic Faston F2 correct?
- They are indeed Faston F2
- **This one is providing the most confusion and trepidation** - Battery delineation: High rate discharge?
- Is the high-rate discharge an imperative? Shops here do not seem to know what I am talking about, and all websites here tend to recommend the “regular” product range of batteries just 12V 12Ah 20HR. and any American or UK websites or eBay listings also tend to be the same, just the usual 12V 12Ah 20HR batteries
- This is a complete over-simplification and limited to my lack of in-depth understanding, please do your own research! : It is strongly recommended. Technically Non-high rate discharge batteries will work, however you may compromise their lifespan, introduce more wear, increase heat dissipation during use and possibly not be able to actually have enough discharge capacity to start up any power hungry machines.
- Trying to find High rate discharge variants here is basically impossible… example Yuasa NP1212 – easily found and what keeps getting recommended as compatible. However Yuasa has a “High rate” series “NPH”….???
- Complete Noob here but doing some calc on the regular 20HR batteries gives me a C-state of 14…which is considered high rate discharge (according to google…I have no clue)
- Basically…… Am I overthinking this and have I been misled by the High rate discharge thing? Should I just make sure it’s a relatively known brand name, is 12V 12Ah+ 20HR VRLA, and does not mention “deep cycle”? and be done with it?
- See 3.1.1. as far as I understand it “deep cycle” means something different. Please do your own research though.
- Am just worried I don’t turn my homelab into a little unsolicited fireworks show if I put in the incorrect type discharge of battery. Please ELI5 if need be, this is a perfect learning opportunity for me
- See 3.1.1.
- Alot of folks mention good sources and brands, but mostly US/UK based
- Any chance someone has relatively reputable brands and or sites for European suppliers?
- Yuasa? Ultracell? Invictus? Anyone familiar with those?
- These seem to be considered reputable brands (at least here in Greece anyway) they are sort of “mid-tier” and have some sort of pedigree
- Other
- Is there something I need to check if and when they arrive?
- Once fully charged, remove them and probe them with a Multi-meter. Below points source: random google-fu, please do your own corroboration and research.
- Compare the measured voltage to the battery’s rated voltage (often 12V for lead-acid batteries).
- A fully charged 12V battery should read around 12.6 to 12.8 volts.
- A voltage below 12.4 volts indicates the battery may be partially discharged.
- A voltage below 12.0 volts suggests the battery is significantly discharged and may need charging or replacement.
- Is there a rudimentary way to check they are in good condition?
- See above 5.1 also just make sure you see nor obvious physical damage
- Is there something specific I need to do after I replace the batteries. either to the batteries themselves or on the ups, like a reset, or conditioning or something? or do I just plug in the new batteries do the little self-test on the ups, update battery change date, and away we go?
- If your ups has one, remove the battery connection coupler cap at the back for safety (this breaks the circuit to the batteries)
- Once you install the batteries, re attached the safety cap, turn on the ups.
- Depending on your make and model it may autodetect a new battery connection and ask for confirmation and for setting the new date for the battery being changed.
- Check you manual for the respective way to do this