Has anyone done this? How are your temps?
Looks like it would be terrible for WC. It is a fire suppressant, which means it would (theoretically) be designed to insulate and not transfer heat, so it'd be like pumping air through your loop, but with even worse thermals, probably. Thickness-wise, as well, it would clog your blocks, pump, and probably stain your tubing. Don't do it.
The particular 3M Novec you are looking for is 7000.
It has a boiling point of 34c and is designed for electronic submerging. Also Novec is not designed to be used in closed systems due to it low boiling point. You require a cold source (such as a water cooled rad or peltier) to cool the gas down back into a liquid.
Like this: http://youtu.be/Z_X_hgtlJpA